6 meter output
Rich McCabe
开云体育Why two breakers? ? From: [email protected] <[email protected]> On Behalf Of JERRY
Sent: Saturday, July 4, 2020 2:58 PM To: [email protected] Subject: Re: [la1k] 6 meter output ? I had an electrician do it. He used 2 20 amp breakers and 12 gauge wire. The draw is supposed to be max 10 amps on the LA-1K I believe? ? 73, Jerry ?
|
George Robbins
The 240 volt power cord from Palstar has the NEMA standard blade arrangement for a 240 volt 20 amp outlet.? The amplifier is spec'ed to draw 10 amps at 240 volts.?
You should install a 240 volt 20 amp branch circuit.? That will require a 2 pole - 20 amp breaker, # 12 AWG wire - typically 12-2 with ground which usually has a yellow sheath, and a 240 volt 20 amp outlet.?? If you went to a 30 amp breaker, you would be required by the NEC to use #10 AWG wire and install a 240 volt 30 amp outlet - which would not allow you plug in the power cord from the Palstar amplifier because of a different (and larger) blade arrangement.? |
Rich McCabe
开云体育Not one 220 breaker?? I do not think two single breakers will pass code anywhere in the US. ? ? ? From: [email protected] <[email protected]> On Behalf Of JERRY
Sent: Saturday, July 4, 2020 3:03 PM To: [email protected] Subject: Re: [la1k] 6 meter output ? He had one on each wire, not sure why all I know he was a commercial electrician. I obviously was not lol |
They are bared together, that’s all I know
toggle quoted message
Show quoted text
?
On Jul 4, 2020, at 13:04, Rich McCabe via groups.io <r.mccabe@...> wrote:
--
73, Jerry |
Rich McCabe
开云体育OK that is one breaker ? ? ? ? From: [email protected] <[email protected]> On Behalf Of JERRY
Sent: Saturday, July 4, 2020 3:06 PM To: [email protected] Subject: Re: [la1k] 6 meter output ? They are bared together, that’s all I know ? 73, Jerry 818.207.6600 ?
|