Why two breakers?

?

From: [email protected] <[email protected]> On Behalf Of JERRY
Sent: Saturday, July 4, 2020 2:58 PM
To: [email protected]
Subject: Re: [la1k] 6 meter output

?

I had an electrician do it. He used 2 20 amp breakers and 12 gauge wire. The draw is supposed to be max 10 amps on the LA-1K I believe?

?

73,

Jerry

?



On Jul 4, 2020, at 12:46, Steve Shep via <shepsvettes@...> wrote:

?Going to install a 220v outlet tomorrow. SHould I go 20 or 30 aMP BREAKER 12-2 OR 10-2 WIRE?


--
73,
Jerry


George Robbins
 

The 240 volt power cord from Palstar has the NEMA standard blade arrangement for a 240 volt 20 amp outlet.? The amplifier is spec'ed to draw 10 amps at 240 volts.?

You should install a 240 volt 20 amp branch circuit.? That will require a 2 pole - 20 amp breaker, # 12 AWG wire - typically 12-2 with ground which usually has a yellow sheath, and a 240 volt 20 amp outlet.??

If you went to a 30 amp breaker, you would be required by the NEC to use #10 AWG wire and install a 240 volt 30 amp outlet - which would not allow you plug in the power cord from the Palstar amplifier because of a different (and larger) blade arrangement.?


 

He had one on each wire, not sure why all I know he was a commercial electrician. I obviously was not lol
--
73,
Jerry


Rich McCabe
 

开云体育

Not one 220 breaker?? I do not think two single breakers will pass code anywhere in the US.

?

?

?

From: [email protected] <[email protected]> On Behalf Of JERRY
Sent: Saturday, July 4, 2020 3:03 PM
To: [email protected]
Subject: Re: [la1k] 6 meter output

?

He had one on each wire, not sure why all I know he was a commercial electrician. I obviously was not lol
--
73,
Jerry


 
Edited

They are bared together, that’s all I know
?

On Jul 4, 2020, at 13:04, Rich McCabe via groups.io <r.mccabe@...> wrote:

Not one 220 breaker?? I do not think two single breakers will pass code anywhere in the US.

?

?

?

From: [email protected] <[email protected]> On Behalf Of JERRY
Sent: Saturday, July 4, 2020 3:03 PM
To: [email protected]
Subject: Re: [la1k] 6 meter output

?

He had one on each wire, not sure why all I know he was a commercial electrician. I obviously was not lol
--
73,
Jerry

?


--
73,
Jerry


Rich McCabe
 

开云体育

OK that is one breaker ?

?

?

?

From: [email protected] <[email protected]> On Behalf Of JERRY
Sent: Saturday, July 4, 2020 3:06 PM
To: [email protected]
Subject: Re: [la1k] 6 meter output

?

They are bared together, that’s all I know

?

73,

Jerry

818.207.6600

?



On Jul 4, 2020, at 13:04, Rich McCabe via <r.mccabe@...> wrote:

?

Not one 220 breaker?? I do not think two single breakers will pass code anywhere in the US.

?

?

?

From: [email protected] <[email protected]> On Behalf Of JERRY
Sent: Saturday, July 4, 2020 3:03 PM
To: [email protected]
Subject: Re: [la1k] 6 meter output

?

He had one on each wire, not sure why all I know he was a commercial electrician. I obviously was not lol
--
73,
Jerry


--
73,
Jerry


 

Did my 220v wiring. I used 10-3 wire so it should be good.