Hello group
does anyone has done bacnet with the vc4. when I add the bacnet device slot it shows ok at the bacnet explorer (yabe), but when I add any hosted object to the program, it neither show the object at the explorer and now I lost the device too at yabe..
I have open, I guess did it well, the port that I am using (47809), but I am not sure if I have to do more stuff at the linux server for letting the bacnet objects to show in the bacnet ecosystem..
any experienced advices?
thanks
nico


 

I thought it was not supported with VC4


 

also: 47808 is the default UDP port for almost everything


 

¿ªÔÆÌåÓý

Ir is supported, it does actually have some values to change at the web explorer settings page
NFH

On 31 Jul 2024, at 12:20?p.m., MQSACK via groups.io <mqsack@...> wrote:

?
I thought it was not supported with VC4


 

¿ªÔÆÌåÓý

It comes with a 100 object license (double the size than the rmc4) and a 1000 Object license can be bought
NFH

On 31 Jul 2024, at 4:14?p.m., nicofreda via groups.io <cdandcontrol@...> wrote:

?Ir is supported, it does actually have some values to change at the web explorer settings page
NFH

On 31 Jul 2024, at 12:20?p.m., MQSACK via groups.io <mqsack@...> wrote:

?
I thought it was not supported with VC4


 

found my error and now working.?
I was leaving by mistake the COV (change of value) of each hosted object in 0, and at the error log I've found that message of "cov value is out of range....". needed a value between 1-65535 :|
that mistake crash all the bacnet process within the processor.?
worked fine now in VC4