Changed the Abuf to Sbuf and there you have it no 0 sent on start!!!
Thanks for the help.
toggle quoted message
Show quoted text
--- In Crestron@..., "constantcharge2" <constantcharge@...> wrote: So I put the scaling into the simpl+ module. Tested and still sent command out issuing a change on init.
I then commented out the Abuf feeding the module and no command sent at init....
It seems to be putting a 0 onto the input once the enable pin is high. (10 sec after init as I already have a delay)
wierd....
--- In Crestron@..., Tray Schaeffer <trayschaeffer@> wrote:
+1 for what Jason just said. I would add that you should also confirm that there is nothing in MAIN that would alter output values at program start.
Tray
-----Original Message----- From: Jason Melvin Sent: Friday, May 17, 2013 10:26 AM To: Crestron@... Subject: Re: [Crestron] Re: Simpl + Change Analog
In your case, since you already have the SIMPL+ module, I agree it makes more sense to either add an enable line or a simple delay before enabling the CHANGE event. You could block it by testing against the enable input or against an internal variable.
On Fri, May 17, 2013 at 9:58 AM, constantcharge2 <constantcharge@>wrote:
**
Ok so looking at wrapper I have a Abuf on input already. that I have a 10 sec delay on before enable but inside this wrapper I have a scaler to convert values before simpl+ module. Could this be throwing out a value at init.... maybe I could do this in simpl+ instead....
--- In Crestron@..., Jason Melvin <jwmelvin@> wrote:
Oh, I think I get it now. From the ABUF help: ----
Analog signals (2-Series and X-Series)
Sets the analog value that will be propagated to the corresponding output with each rising edge of <enable>. If the input/output pair contains the same analog value, the analog input will still be propagated.
If an analog input changes value or is re-propagated while <enable> is high, the value will only be propagated to the corresponding output if the
output has a different value.
----
So, ABUF will prevent a repeating loop when held enabled but SBUF prevents
propagating when enabled. I used SBUF because when I enable the buffer, I don't want a signal sent. That said, I could probably tolerate analogs propagating once the input value is correct, or could use an AOS to determine when to propagate a real signal. Thanks for the pointers Steve.
On Fri, May 17, 2013 at 9:32 AM, Jason Melvin <jwmelvin@> wrote:
Hm, I thought the behavior was exactly the opposite, because of the statement in ABUF help: "If the input/output pair contains the same analog
value, the analog input will still be propagated."
I have, however, seen a loop created with SBUF and analog signals, so the
same signal continuously propagages and repropagates. Perhaps there is some
subtlety that I am missing.
On Fri, May 17, 2013 at 8:57 AM, Steve Kaudle <skaudle@> wrote:
**
A buffer can certainly help, but I'd typically recommend using a ABUF
(as
opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way
you
eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have
the
added benefit of the ABUF's ability to eliminate unwanted
repropigations
when the output already matches the input, further reducing the
number of
unwanted SIMPL+ Change events.
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on
boot.
That way, the initially 0 analog signals don't cause switchers to
change
sources before the old settings get recalled from memory. The SBUF
blocks
serial and analog signals that would otherwise go to devices. Also, a
BUF
signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor.
On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@> wrote:
**
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input
to
propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in
an
IF statement to prevent a transition of the output you don't want,
but
it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to
stop
this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
[Non-text portions of this message have been removed]
------------------------------------
*
****
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
*
****Yahoo! Groups Links
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
------------------------------------
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area. Yahoo! Groups Links
|
So I put the scaling into the simpl+ module. Tested and still sent command out issuing a change on init.
I then commented out the Abuf feeding the module and no command sent at init....
It seems to be putting a 0 onto the input once the enable pin is high. (10 sec after init as I already have a delay)
wierd....
toggle quoted message
Show quoted text
--- In Crestron@..., Tray Schaeffer <trayschaeffer@...> wrote: +1 for what Jason just said. I would add that you should also confirm that there is nothing in MAIN that would alter output values at program start.
Tray
-----Original Message----- From: Jason Melvin Sent: Friday, May 17, 2013 10:26 AM To: Crestron@... Subject: Re: [Crestron] Re: Simpl + Change Analog
In your case, since you already have the SIMPL+ module, I agree it makes more sense to either add an enable line or a simple delay before enabling the CHANGE event. You could block it by testing against the enable input or against an internal variable.
On Fri, May 17, 2013 at 9:58 AM, constantcharge2 <constantcharge@...>wrote:
**
Ok so looking at wrapper I have a Abuf on input already. that I have a 10 sec delay on before enable but inside this wrapper I have a scaler to convert values before simpl+ module. Could this be throwing out a value at init.... maybe I could do this in simpl+ instead....
--- In Crestron@..., Jason Melvin <jwmelvin@> wrote:
Oh, I think I get it now. From the ABUF help: ----
Analog signals (2-Series and X-Series)
Sets the analog value that will be propagated to the corresponding output with each rising edge of <enable>. If the input/output pair contains the same analog value, the analog input will still be propagated.
If an analog input changes value or is re-propagated while <enable> is high, the value will only be propagated to the corresponding output if the
output has a different value.
----
So, ABUF will prevent a repeating loop when held enabled but SBUF prevents
propagating when enabled. I used SBUF because when I enable the buffer, I don't want a signal sent. That said, I could probably tolerate analogs propagating once the input value is correct, or could use an AOS to determine when to propagate a real signal. Thanks for the pointers Steve.
On Fri, May 17, 2013 at 9:32 AM, Jason Melvin <jwmelvin@> wrote:
Hm, I thought the behavior was exactly the opposite, because of the statement in ABUF help: "If the input/output pair contains the same analog
value, the analog input will still be propagated."
I have, however, seen a loop created with SBUF and analog signals, so the
same signal continuously propagages and repropagates. Perhaps there is some
subtlety that I am missing.
On Fri, May 17, 2013 at 8:57 AM, Steve Kaudle <skaudle@> wrote:
**
A buffer can certainly help, but I'd typically recommend using a ABUF
(as
opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way
you
eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have
the
added benefit of the ABUF's ability to eliminate unwanted
repropigations
when the output already matches the input, further reducing the
number of
unwanted SIMPL+ Change events.
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on
boot.
That way, the initially 0 analog signals don't cause switchers to
change
sources before the old settings get recalled from memory. The SBUF
blocks
serial and analog signals that would otherwise go to devices. Also, a
BUF
signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor.
On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@> wrote:
**
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input
to
propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in
an
IF statement to prevent a transition of the output you don't want,
but
it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to
stop
this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
------------------------------------
*
****
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
*
****Yahoo! Groups Links
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
------------------------------------
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area. Yahoo! Groups Links
|
+1 for what Jason just said. I would add that you should also confirm that there is nothing in MAIN that would alter output values at program start.
Tray
toggle quoted message
Show quoted text
-----Original Message----- From: Jason Melvin Sent: Friday, May 17, 2013 10:26 AM To: Crestron@... Subject: Re: [Crestron] Re: Simpl + Change Analog In your case, since you already have the SIMPL+ module, I agree it makes more sense to either add an enable line or a simple delay before enabling the CHANGE event. You could block it by testing against the enable input or against an internal variable. On Fri, May 17, 2013 at 9:58 AM, constantcharge2 <constantcharge@...>wrote: **
Ok so looking at wrapper I have a Abuf on input already. that I have a 10 sec delay on before enable but inside this wrapper I have a scaler to convert values before simpl+ module. Could this be throwing out a value at init.... maybe I could do this in simpl+ instead....
--- In Crestron@..., Jason Melvin <jwmelvin@...> wrote:
Oh, I think I get it now. From the ABUF help: ----
Analog signals (2-Series and X-Series)
Sets the analog value that will be propagated to the corresponding output with each rising edge of <enable>. If the input/output pair contains the same analog value, the analog input will still be propagated.
If an analog input changes value or is re-propagated while <enable> is high, the value will only be propagated to the corresponding output if the
output has a different value.
----
So, ABUF will prevent a repeating loop when held enabled but SBUF prevents
propagating when enabled. I used SBUF because when I enable the buffer, I don't want a signal sent. That said, I could probably tolerate analogs propagating once the input value is correct, or could use an AOS to determine when to propagate a real signal. Thanks for the pointers Steve.
On Fri, May 17, 2013 at 9:32 AM, Jason Melvin <jwmelvin@...> wrote:
Hm, I thought the behavior was exactly the opposite, because of the statement in ABUF help: "If the input/output pair contains the same analog
value, the analog input will still be propagated."
I have, however, seen a loop created with SBUF and analog signals, so the
same signal continuously propagages and repropagates. Perhaps there is some
subtlety that I am missing.
On Fri, May 17, 2013 at 8:57 AM, Steve Kaudle <skaudle@...> wrote:
**
A buffer can certainly help, but I'd typically recommend using a ABUF
(as
opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way
you
eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have
the
added benefit of the ABUF's ability to eliminate unwanted
repropigations
when the output already matches the input, further reducing the
number of
unwanted SIMPL+ Change events.
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on
boot.
That way, the initially 0 analog signals don't cause switchers to
change
sources before the old settings get recalled from memory. The SBUF
blocks
serial and analog signals that would otherwise go to devices. Also, a
BUF
signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor.
On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@...> wrote:
**
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input
to
propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in
an
IF statement to prevent a transition of the output you don't want,
but
it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to
stop
this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
------------------------------------
*
****
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
*
****Yahoo! Groups Links
------------------------------------ Check out the Files area for useful modules, documents, and drivers. A contact list of Crestron dealers and programmers can be found in the Database area. Yahoo! Groups Links
|
In your case, since you already have the SIMPL+ module, I agree it makes more sense to either add an enable line or a simple delay before enabling the CHANGE event. You could block it by testing against the enable input or against an internal variable. On Fri, May 17, 2013 at 9:58 AM, constantcharge2 <constantcharge@...>wrote: **
Ok so looking at wrapper I have a Abuf on input already. that I have a 10 sec delay on before enable but inside this wrapper I have a scaler to convert values before simpl+ module. Could this be throwing out a value at init.... maybe I could do this in simpl+ instead....
--- In Crestron@..., Jason Melvin <jwmelvin@...> wrote:
Oh, I think I get it now. From the ABUF help: ----
Analog signals (2-Series and X-Series)
Sets the analog value that will be propagated to the corresponding output with each rising edge of <enable>. If the input/output pair contains the same analog value, the analog input will still be propagated.
If an analog input changes value or is re-propagated while <enable> is high, the value will only be propagated to the corresponding output if the
output has a different value.
----
So, ABUF will prevent a repeating loop when held enabled but SBUF prevents
propagating when enabled. I used SBUF because when I enable the buffer, I don't want a signal sent. That said, I could probably tolerate analogs propagating once the input value is correct, or could use an AOS to determine when to propagate a real signal. Thanks for the pointers Steve.
On Fri, May 17, 2013 at 9:32 AM, Jason Melvin <jwmelvin@...> wrote:
Hm, I thought the behavior was exactly the opposite, because of the statement in ABUF help: "If the input/output pair contains the same analog
value, the analog input will still be propagated."
I have, however, seen a loop created with SBUF and analog signals, so the
same signal continuously propagages and repropagates. Perhaps there is some
subtlety that I am missing.
On Fri, May 17, 2013 at 8:57 AM, Steve Kaudle <skaudle@...> wrote:
**
A buffer can certainly help, but I'd typically recommend using a ABUF
(as
opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way
you
eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have
the
added benefit of the ABUF's ability to eliminate unwanted
repropigations
when the output already matches the input, further reducing the
number of
unwanted SIMPL+ Change events.
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on
boot.
That way, the initially 0 analog signals don't cause switchers to
change
sources before the old settings get recalled from memory. The SBUF
blocks
serial and analog signals that would otherwise go to devices. Also, a
BUF
signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor.
On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@...> wrote:
**
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input
to
propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in
an
IF statement to prevent a transition of the output you don't want,
but
it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to
stop
this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
[Non-text portions of this message have been removed]
------------------------------------
*
****
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
*
****Yahoo! Groups Links
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
|
Ok so looking at wrapper I have a Abuf on input already. that I have a 10 sec delay on before enable but inside this wrapper I have a scaler to convert values before simpl+ module. Could this be throwing out a value at init.... maybe I could do this in simpl+ instead....
toggle quoted message
Show quoted text
--- In Crestron@..., Jason Melvin <jwmelvin@...> wrote: Oh, I think I get it now. From the ABUF help: ----
Analog signals (2-Series and X-Series)
Sets the analog value that will be propagated to the corresponding output with each rising edge of <enable>. If the input/output pair contains the same analog value, the analog input will still be propagated.
If an analog input changes value or is re-propagated while <enable> is high, the value will only be propagated to the corresponding output if the output has a different value.
----
So, ABUF will prevent a repeating loop when held enabled but SBUF prevents propagating when enabled. I used SBUF because when I enable the buffer, I don't want a signal sent. That said, I could probably tolerate analogs propagating once the input value is correct, or could use an AOS to determine when to propagate a real signal. Thanks for the pointers Steve.
On Fri, May 17, 2013 at 9:32 AM, Jason Melvin <jwmelvin@...> wrote:
Hm, I thought the behavior was exactly the opposite, because of the statement in ABUF help: "If the input/output pair contains the same analog value, the analog input will still be propagated."
I have, however, seen a loop created with SBUF and analog signals, so the same signal continuously propagages and repropagates. Perhaps there is some subtlety that I am missing.
On Fri, May 17, 2013 at 8:57 AM, Steve Kaudle <skaudle@...> wrote:
**
A buffer can certainly help, but I'd typically recommend using a ABUF (as opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way you eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have the added benefit of the ABUF's ability to eliminate unwanted repropigations when the output already matches the input, further reducing the number of unwanted SIMPL+ Change events.
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on boot. That way, the initially 0 analog signals don't cause switchers to change sources before the old settings get recalled from memory. The SBUF blocks serial and analog signals that would otherwise go to devices. Also, a BUF signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor.
On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@...> wrote:
**
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input to propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in an IF statement to prevent a transition of the output you don't want, but it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to stop this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
------------------------------------
*
****
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
* ****Yahoo! Groups Links
[Non-text portions of this message have been removed]
|
Oh, I think I get it now. From the ABUF help: ----
Analog signals (2-Series and X-Series)
Sets the analog value that will be propagated to the corresponding output with each rising edge of <enable>. If the input/output pair contains the same analog value, the analog input will still be propagated.
If an analog input changes value or is re-propagated while <enable> is high, the value will only be propagated to the corresponding output if the output has a different value.
----
So, ABUF will prevent a repeating loop when held enabled but SBUF prevents propagating when enabled. I used SBUF because when I enable the buffer, I don't want a signal sent. That said, I could probably tolerate analogs propagating once the input value is correct, or could use an AOS to determine when to propagate a real signal. Thanks for the pointers Steve.
toggle quoted message
Show quoted text
On Fri, May 17, 2013 at 9:32 AM, Jason Melvin <jwmelvin@...> wrote: Hm, I thought the behavior was exactly the opposite, because of the statement in ABUF help: "If the input/output pair contains the same analog value, the analog input will still be propagated."
I have, however, seen a loop created with SBUF and analog signals, so the same signal continuously propagages and repropagates. Perhaps there is some subtlety that I am missing.
On Fri, May 17, 2013 at 8:57 AM, Steve Kaudle <skaudle@...> wrote:
**
A buffer can certainly help, but I'd typically recommend using a ABUF (as opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way you eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have the added benefit of the ABUF's ability to eliminate unwanted repropigations when the output already matches the input, further reducing the number of unwanted SIMPL+ Change events.
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on boot. That way, the initially 0 analog signals don't cause switchers to change sources before the old settings get recalled from memory. The SBUF blocks serial and analog signals that would otherwise go to devices. Also, a BUF signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor.
On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@...> wrote:
**
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input to propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in an IF statement to prevent a transition of the output you don't want, but it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to stop this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
------------------------------------
*
****
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
* ****Yahoo! Groups Links
|
Thanks for the reply's,
Will have a look at the wrapper for my simpl+ module. Also will have a look into buffers.
toggle quoted message
Show quoted text
--- In Crestron@..., Jason Melvin <jwmelvin@...> wrote: Hm, I thought the behavior was exactly the opposite, because of the statement in ABUF help: "If the input/output pair contains the same analog value, the analog input will still be propagated."
I have, however, seen a loop created with SBUF and analog signals, so the same signal continuously propagages and repropagates. Perhaps there is some subtlety that I am missing.
On Fri, May 17, 2013 at 8:57 AM, Steve Kaudle <skaudle@...> wrote:
**
A buffer can certainly help, but I'd typically recommend using a ABUF (as opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way you eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have the added benefit of the ABUF's ability to eliminate unwanted repropigations when the output already matches the input, further reducing the number of unwanted SIMPL+ Change events.
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on boot. That way, the initially 0 analog signals don't cause switchers to change sources before the old settings get recalled from memory. The SBUF blocks serial and analog signals that would otherwise go to devices. Also, a BUF signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor.
On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@...> wrote:
**
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input to propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in an IF statement to prevent a transition of the output you don't want, but it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to stop this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
------------------------------------
*
****
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
* ****Yahoo! Groups Links
[Non-text portions of this message have been removed]
|
Hm, I thought the behavior was exactly the opposite, because of the statement in ABUF help: "If the input/output pair contains the same analog value, the analog input will still be propagated."
I have, however, seen a loop created with SBUF and analog signals, so the same signal continuously propagages and repropagates. Perhaps there is some subtlety that I am missing.
toggle quoted message
Show quoted text
On Fri, May 17, 2013 at 8:57 AM, Steve Kaudle <skaudle@...> wrote: **
A buffer can certainly help, but I'd typically recommend using a ABUF (as opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way you eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have the added benefit of the ABUF's ability to eliminate unwanted repropigations when the output already matches the input, further reducing the number of unwanted SIMPL+ Change events.
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on boot. That way, the initially 0 analog signals don't cause switchers to change sources before the old settings get recalled from memory. The SBUF blocks serial and analog signals that would otherwise go to devices. Also, a BUF signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor.
On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@...> wrote:
**
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input to propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in an IF statement to prevent a transition of the output you don't want, but it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to stop this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
------------------------------------
*
****
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
* ****Yahoo! Groups Links
|
A buffer can certainly help, but I'd typically recommend using a ABUF (as opposed to the SBUF) and latching the enable only after an honest-to-goodness change has been generated in the logic. This way you eliminate what is probably a superfluous Change event from running automatically (either at boot or sometime thereafter), and you have the added benefit of the ABUF's ability to eliminate unwanted repropigations when the output already matches the input, further reducing the number of unwanted SIMPL+ Change events.
toggle quoted message
Show quoted text
-----Original Message----- From: Crestron@... [mailto:Crestron@...] On Behalf Of Jason Melvin Sent: Friday, May 17, 2013 8:22 AM To: Crestron@... Subject: Re: [Crestron] Simpl + Change Analog I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on boot. That way, the initially 0 analog signals don't cause switchers to change sources before the old settings get recalled from memory. The SBUF blocks serial and analog signals that would otherwise go to devices. Also, a BUF signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor. On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@...> wrote: **
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input to propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in an IF statement to prevent a transition of the output you don't want, but it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to stop this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
------------------------------------ * **** Check out the Files area for useful modules, documents, and drivers. A contact list of Crestron dealers and programmers can be found in the Database area. * ****Yahoo! Groups Links
|
I use an SBUF in SIMPL for this, which gets enabled after ~10 sec on boot. That way, the initially 0 analog signals don't cause switchers to change sources before the old settings get recalled from memory. The SBUF blocks serial and analog signals that would otherwise go to devices. Also, a BUF signal prevents the program from triggering motion-detector logic for contact-closure-output detectors, which have inverted logic due to the pullup resistor. On Fri, May 17, 2013 at 7:20 AM, Steve Kaudle <skaudle@...> wrote: **
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input to propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in an IF statement to prevent a transition of the output you don't want, but it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to stop this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
|
The only SIMPL+ 'event' that will automatically run when the program is initialized is the Main, so if your Change is running at bootup it's because something is causing the analog connected to the input to propagate a zero at bootup (IE: the issue is in your SIMPLWindows code).
There's nothing wrong with encapsulating the output calculation in an IF statement to prevent a transition of the output you don't want, but it won't do anything to prevent the unnecessary SIMPL+ thread from being generated. I'd concentrate my efforts on preventing the input analog from propagating at bootup.
From: Crestron@... [mailto:Crestron@...] On Behalf Of constantcharge2 Sent: Friday, May 17, 2013 2:33 AM To: Crestron@... Subject: [Crestron] Simpl + Change Analog
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to stop this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
|
Hi All,
Have a issue that has me stumped. using the below
Change Analog_in { Print("Analog_in %d \n",Analog_in); Level$ = IToHex(Analog_In); }
When program initializes it enters this module and outputs unwanted code eg sets hex levels to 0. (turns off amp's) Is there a way to stop this happening?
my only way of fixing this currently is to do a feedback loop eg
Change Analog_in { Print("Analog_in %d \n",Analog_in); if (Analog_in <> Current_Level) { Level$ = IToHex(Analog_In); } }
|