开云体育

ctrl + shift + ? for shortcuts
© 2025 Groups.io

Best RGBWW controller for led light strip...


 

What are you guys using for controlling rgbww led lighting? ?Need IP hardwired or wireless not rs232 based.


 

Crestron themselves have a couple controllers we like to use for LED Tape.?

Both wired and wireless
CLC-1LEDPWM-RGBW-EX
DIN-2LEDPWM8

if we need a deeper level of presets or show control we’ll put something like a Cueserver and DMX LED driver in line. Then just use the crestron to fire the scenes. ?


—碍测濒别


 

Sadly, both those solutions are only designed for four-channel RGBW. Perhaps Crestron will bring out something soon to address the trend for five-channel RGBWW.

What are people using as a low cost solution to interface with DMX?


 

开云体育

Hi,

depends on what you call ?low cost“.

I?m using Enttec ?Ethernet gateways

or with PoE

for smaller installation.

Can be easily controlled via Crestron SACN-module.

Regards, Thorsten

?

Von: [email protected] <[email protected]> Im Auftrag von rickwookie
Gesendet: Samstag, 30. Mai 2020 19:32
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

Sadly, both those solutions are only designed for four-channel RGBW. Perhaps Crestron will bring out something soon to address the trend for five-channel RGBWW.

What are people using as a low cost solution to interface with DMX?


 

Is sACN a standard, i.e. will the Crestron sACN module work with any interface that supports it? Reason I ask, this little thing claims to support ArtNet and sACN, so if I can control it easily, I may give it a try. It’s about half the price of the Enttec interface.?


 

开云体育

Looks good to me – in my opinion, it should work.

Thanks for pointing out – if it works it could be a good option for me as well. J

?

Von: [email protected] <[email protected]> Im Auftrag von rickwookie
Gesendet: Samstag, 30. Mai 2020 21:52
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

Is sACN a standard, i.e. will the Crestron sACN module work with any interface that supports it? Reason I ask, this little thing claims to support ArtNet and sACN, so if I can control it easily, I may give it a try. It’s about half the price of the Enttec interface.?


 
Edited

Will report back when I’ve tried it.

To the OP if you go DMX, this is an example of a 5-channel decoder with a fairly high current capacity. You may find it more economical to use a pair of lower cost 3-Chanel DMX decoder drivers, and just use two of the three channels on the second one for the WW/CW output.


 

开云体育


sACN is a protocol standard albeit there were some earlier versions that weren’t quite released. But almost everything made now should all be compatible. You can use other manufactures DMX gateways for DMX out’s. If you want a good budget friendly unit which works well, look at?. They work pretty well.?


On May 30, 2020, at 1:27 PM, rickwookie <rickwookie@...> wrote:

Will report back when I’ve tried it.


 

开云体育

Sunricher SR-2108B-M5-5...

Sunricher is the OEM manufacturer for most LED/color tuning tapelight “manufacturers”. They’re $90 on Amazon.

RGBWW is trash for tunable white color accuracy. Not accurate to black body curve and for high end troffers and linear based fixtures there are better solutions... just more expensive and you have to hand the chipset to the fixture assembler... or better yet, just do it yourself.

Also, don’t skimp on the DMX controller. I’ve used the Enttecs and other cheaper solutions and when we are pushing lighting scenes carrying dozens of addresses you get inconsistent response - popcorning, level control issues. Go commercial grade for multiple load control. DMX is our main lighting control infrastructure for everything.

On May 30, 2020, at 1:43 PM, rickwookie <rickwookie@...> wrote:

?

[Edited Message Follows]

Will report back when I’ve tried it.

To the OP if you go DMX, this is an example of a 5-channel decoder with a fairly high current capacity. You may find it more economical to use a pair of lower cost 3-Chanel DMX decoder drivers, and just use two of the three channels on the second one for the WW/CW output.


 

Ah gotchya. I read the WW as Warm White instead of 2 separate channels.?


in that case +1 for going the sACN route.?


sACN is a standard of DMX over IP supported by many manufacturers.?


 

开云体育

Great — keep us posted on this. ?I’ll also look into the Crestron option. ?I like the idea of the ethernet based on… I was even thinking of using an H801 flash with Tasmota and then just controlling via HTTP — but I’d rather have a more “commercial” solution.?

On May 30, 2020, at 1:27 PM, rickwookie <rickwookie@...> wrote:

[Edited Message Follows]

Will report back when I’ve tried it.

To the OP if you go DMX, this is an example of a 5-channel decoder with a fairly high current capacity. You may find it more economical to use a pair of lower cost 3-Chanel DMX decoder drivers, and just use two of the three channels on the second one for the WW/CW output.



 

开云体育

Very interesting.

In terms of stripes I?d go for separates as well. You can get CCT-stripes with much better light quality (CRI>90) and lumen as separates compared to combined stripes.

?

Could you elaborate a bit on the lights? What products do you use?

Also on commercial grade controllers?

?

Thanks.

?

?

?

Von: [email protected] <[email protected]> Im Auftrag von Pixels Bits
Gesendet: Samstag, 30. Mai 2020 23:16
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

Sunricher SR-2108B-M5-5...

?

Sunricher is the OEM manufacturer for most LED/color tuning tapelight “manufacturers”. They’re $90 on Amazon.

?

RGBWW is trash for tunable white color accuracy. Not accurate to black body curve and for high end troffers and linear based fixtures there are better solutions... just more expensive and you have to hand the chipset to the fixture assembler... or better yet, just do it yourself.

?

Also, don’t skimp on the DMX controller. I’ve used the Enttecs and other cheaper solutions and when we are pushing lighting scenes carrying dozens of addresses you get inconsistent response - popcorning, level control issues. Go commercial grade for multiple load control. DMX is our main lighting control infrastructure for everything.



On May 30, 2020, at 1:43 PM, rickwookie <rickwookie@...> wrote:

?

[Edited Message Follows]

Will report back when I’ve tried it.

To the OP if you go DMX, this is an example of a 5-channel decoder with a fairly high current capacity. You may find it more economical to use a pair of lower cost 3-Chanel DMX decoder drivers, and just use two of the three channels on the second one for the WW/CW output.


 

I think the H801 looks like a really interesting little device. Do you know if it can be flashed with Tasmota using tuya-convert, or only by opening it up and reflashing via the pcb header?


 

开云体育

Oh, and to control the Sunricher device you mentioned, you need an additional DMX gateway to be able to control it via Crestron, so that?s on top.

?

?

Von: [email protected] <[email protected]> Im Auftrag von Pixels Bits
Gesendet: Samstag, 30. Mai 2020 23:16
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

Sunricher SR-2108B-M5-5...

?

Sunricher is the OEM manufacturer for most LED/color tuning tapelight “manufacturers”. They’re $90 on Amazon.

?

RGBWW is trash for tunable white color accuracy. Not accurate to black body curve and for high end troffers and linear based fixtures there are better solutions... just more expensive and you have to hand the chipset to the fixture assembler... or better yet, just do it yourself.

?

Also, don’t skimp on the DMX controller. I’ve used the Enttecs and other cheaper solutions and when we are pushing lighting scenes carrying dozens of addresses you get inconsistent response - popcorning, level control issues. Go commercial grade for multiple load control. DMX is our main lighting control infrastructure for everything.



On May 30, 2020, at 1:43 PM, rickwookie <rickwookie@...> wrote:

?

[Edited Message Follows]

Will report back when I’ve tried it.

To the OP if you go DMX, this is an example of a 5-channel decoder with a fairly high current capacity. You may find it more economical to use a pair of lower cost 3-Chanel DMX decoder drivers, and just use two of the three channels on the second one for the WW/CW output.


 

开云体育

CRI is for the static colors. Not the color combinations that tend towards CRI 80... CRI is also an antiquated methodology for color rendering anyways. IES has adopted TM-30 which has a higher number of color samples for evaluating color accuracy - 18 vs 99.

In addition, tunable white systems are evaluated based on accuracy to black body curve. Tunable white using CW/WW is tuning color based on color combination of two points on a line - 2700K and 6500K. Lines can’t hit points all points on a curve. In addition, color combinations of 3 primaries and white aren’t color accurate, the guys at Solid state lighting research department at the PNNL have shown that to get any modicum of accuracy along the black body curve you need at least 4 primary colors - like Ketra (RGB+Lime) - the more the better, 7, 9, 12, 24. Sunlight is a combination of multiple wavelengths not just RGB, tech is getting us close to more narrow band control of lighting.

Commercial meaning Enttec show controllers, ETC, Pharos, Color Kinetics... RDM utilization is killer so SACN is insufficient and you really should be using ArtNet for bidirectional communication. Most downlights I used have iBeacon built in so I can do Bluetooth/RSSI evaluations to know where people are, feedback on thermal output, LED degradation, hour usage... Data data data. There are some chipsets in the process of building in motion sensing based on BLE wave evaluation rather than having to use PIR. You’re talking about true digital light fixtures with firmware upgrades and the ability to have functionalities added to them.

Exciting times.

On May 31, 2020, at 1:13 AM, Thorsten K?hler <thorsten.koehler@...> wrote:

?

Oh, and to control the Sunricher device you mentioned, you need an additional DMX gateway to be able to control it via Crestron, so that?s on top.

?

?

Von: [email protected] <[email protected]> Im Auftrag von Pixels Bits
Gesendet: Samstag, 30. Mai 2020 23:16
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

Sunricher SR-2108B-M5-5...

?

Sunricher is the OEM manufacturer for most LED/color tuning tapelight “manufacturers”. They’re $90 on Amazon.

?

RGBWW is trash for tunable white color accuracy. Not accurate to black body curve and for high end troffers and linear based fixtures there are better solutions... just more expensive and you have to hand the chipset to the fixture assembler... or better yet, just do it yourself.

?

Also, don’t skimp on the DMX controller. I’ve used the Enttecs and other cheaper solutions and when we are pushing lighting scenes carrying dozens of addresses you get inconsistent response - popcorning, level control issues. Go commercial grade for multiple load control. DMX is our main lighting control infrastructure for everything.



On May 30, 2020, at 1:43 PM, rickwookie <rickwookie@...> wrote:

?

[Edited Message Follows]

Will report back when I’ve tried it.

To the OP if you go DMX, this is an example of a 5-channel decoder with a fairly high current capacity. You may find it more economical to use a pair of lower cost 3-Chanel DMX decoder drivers, and just use two of the three channels on the second one for the WW/CW output.


 

开云体育

Yes you need a controller on top of a decoder. You need something that’s going to talk DMX on the system so Crestron can control it. Same with DALI... Crestron doesn’t have an integrated DMX master like Medialon does.

And also those things do 5 amps across each color... the RGBWW tape light I use consumes 10 W/ft max using all colors meaning which means you can get 12’ off one of the decoders. If you need multiple decoders and they have to have something to manage communication as they can’t all just be masters.

On May 31, 2020, at 1:13 PM, Pixels Bits via groups.io <george@...> wrote:

?
CRI is for the static colors. Not the color combinations that tend towards CRI 80... CRI is also an antiquated methodology for color rendering anyways. IES has adopted TM-30 which has a higher number of color samples for evaluating color accuracy - 18 vs 99.

In addition, tunable white systems are evaluated based on accuracy to black body curve. Tunable white using CW/WW is tuning color based on color combination of two points on a line - 2700K and 6500K. Lines can’t hit points all points on a curve. In addition, color combinations of 3 primaries and white aren’t color accurate, the guys at Solid state lighting research department at the PNNL have shown that to get any modicum of accuracy along the black body curve you need at least 4 primary colors - like Ketra (RGB+Lime) - the more the better, 7, 9, 12, 24. Sunlight is a combination of multiple wavelengths not just RGB, tech is getting us close to more narrow band control of lighting.

Commercial meaning Enttec show controllers, ETC, Pharos, Color Kinetics... RDM utilization is killer so SACN is insufficient and you really should be using ArtNet for bidirectional communication. Most downlights I used have iBeacon built in so I can do Bluetooth/RSSI evaluations to know where people are, feedback on thermal output, LED degradation, hour usage... Data data data. There are some chipsets in the process of building in motion sensing based on BLE wave evaluation rather than having to use PIR. You’re talking about true digital light fixtures with firmware upgrades and the ability to have functionalities added to them.

Exciting times.

On May 31, 2020, at 1:13 AM, Thorsten K?hler <thorsten.koehler@...> wrote:

?

Oh, and to control the Sunricher device you mentioned, you need an additional DMX gateway to be able to control it via Crestron, so that?s on top.

?

?

Von: [email protected] <[email protected]> Im Auftrag von Pixels Bits
Gesendet: Samstag, 30. Mai 2020 23:16
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

Sunricher SR-2108B-M5-5...

?

Sunricher is the OEM manufacturer for most LED/color tuning tapelight “manufacturers”. They’re $90 on Amazon.

?

RGBWW is trash for tunable white color accuracy. Not accurate to black body curve and for high end troffers and linear based fixtures there are better solutions... just more expensive and you have to hand the chipset to the fixture assembler... or better yet, just do it yourself.

?

Also, don’t skimp on the DMX controller. I’ve used the Enttecs and other cheaper solutions and when we are pushing lighting scenes carrying dozens of addresses you get inconsistent response - popcorning, level control issues. Go commercial grade for multiple load control. DMX is our main lighting control infrastructure for everything.



On May 30, 2020, at 1:43 PM, rickwookie <rickwookie@...> wrote:

?

[Edited Message Follows]

Will report back when I’ve tried it.

To the OP if you go DMX, this is an example of a 5-channel decoder with a fairly high current capacity. You may find it more economical to use a pair of lower cost 3-Chanel DMX decoder drivers, and just use two of the three channels on the second one for the WW/CW output.


 

开云体育

Interesting information, thanks for sharing. I think I need to get an update on the LED stuff ;-)

Regarding hardware, i?m doing just residential installations, so most of what you mention seems to be over the top for me.

?

?

Von: [email protected] <[email protected]> Im Auftrag von Pixels Bits
Gesendet: Sonntag, 31. Mai 2020 22:13
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

CRI is for the static colors. Not the color combinations that tend towards CRI 80... CRI is also an antiquated methodology for color rendering anyways. IES has adopted TM-30 which has a higher number of color samples for evaluating color accuracy - 18 vs 99.

?

In addition, tunable white systems are evaluated based on accuracy to black body curve. Tunable white using CW/WW is tuning color based on color combination of two points on a line - 2700K and 6500K. Lines can’t hit points all points on a curve. In addition, color combinations of 3 primaries and white aren’t color accurate, the guys at Solid state lighting research department at the PNNL have shown that to get any modicum of accuracy along the black body curve you need at least 4 primary colors - like Ketra (RGB+Lime) - the more the better, 7, 9, 12, 24. Sunlight is a combination of multiple wavelengths not just RGB, tech is getting us close to more narrow band control of lighting.

?

Commercial meaning Enttec show controllers, ETC, Pharos, Color Kinetics... RDM utilization is killer so SACN is insufficient and you really should be using ArtNet for bidirectional communication. Most downlights I used have iBeacon built in so I can do Bluetooth/RSSI evaluations to know where people are, feedback on thermal output, LED degradation, hour usage... Data data data. There are some chipsets in the process of building in motion sensing based on BLE wave evaluation rather than having to use PIR. You’re talking about true digital light fixtures with firmware upgrades and the ability to have functionalities added to them.

?

Exciting times.



On May 31, 2020, at 1:13 AM, Thorsten K?hler <thorsten.koehler@...> wrote:

?

Oh, and to control the Sunricher device you mentioned, you need an additional DMX gateway to be able to control it via Crestron, so that?s on top.

?

?

Von: [email protected] <[email protected]> Im Auftrag von Pixels Bits
Gesendet: Samstag, 30. Mai 2020 23:16
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

Sunricher SR-2108B-M5-5...

?

Sunricher is the OEM manufacturer for most LED/color tuning tapelight “manufacturers”. They’re $90 on Amazon.

?

RGBWW is trash for tunable white color accuracy. Not accurate to black body curve and for high end troffers and linear based fixtures there are better solutions... just more expensive and you have to hand the chipset to the fixture assembler... or better yet, just do it yourself.

?

Also, don’t skimp on the DMX controller. I’ve used the Enttecs and other cheaper solutions and when we are pushing lighting scenes carrying dozens of addresses you get inconsistent response - popcorning, level control issues. Go commercial grade for multiple load control. DMX is our main lighting control infrastructure for everything.




On May 30, 2020, at 1:43 PM, rickwookie <rickwookie@...> wrote:

?

[Edited Message Follows]

Will report back when I’ve tried it.

To the OP if you go DMX, this is an example of a 5-channel decoder with a fairly high current capacity. You may find it more economical to use a pair of lower cost 3-Chanel DMX decoder drivers, and just use two of the three channels on the second one for the WW/CW output.


 

开云体育

When I bought RGBWW strips they were RGB and warm white, with a cool white variant also available labeled as RGBW.?? .?? .??

?

From: <[email protected]> on behalf of "Kyle Goyer via groups.io" <Kyle.goyer@...>
Reply-To: <[email protected]>
Date: Saturday, May 30, 2020 at 2:39 PM
To: <[email protected]>
Subject: Re: [crestron] Best RGBWW controller for led light strip...

?

Ah gotchya. I read the WW as Warm White instead of 2 separate channels.?


in that case +1 for going the sACN route.?


sACN is a standard of DMX over IP supported by many manufacturers.?


 

开云体育

RGB + Dualwhite are also labeled ?RGBCCT“ or ?RGB+CCT“.

?

?

Von: [email protected] <[email protected]> Im Auftrag von MSTC
Gesendet: Dienstag, 2. Juni 2020 04:09
An: [email protected]
Betreff: Re: [crestron] Best RGBWW controller for led light strip...

?

When I bought RGBWW strips they were RGB and warm white, with a cool white variant also available labeled as RGBW.?? .?? .??

?

From: <[email protected]> on behalf of "Kyle Goyer via groups.io" <Kyle.goyer@...>
Reply-To: <[email protected]>
Date: Saturday, May 30, 2020 at 2:39 PM
To: <[email protected]>
Subject: Re: [crestron] Best RGBWW controller for led light strip...

?

Ah gotchya. I read the WW as Warm White instead of 2 separate channels.?


in that case +1 for going the sACN route.?


sACN is a standard of DMX over IP supported by many manufacturers.?


 

开云体育

There is also something called a power repeater that can be employed if your load exceeds the rating on the controller . . .

?

From: <[email protected]> on behalf of "Kyle Goyer via groups.io" <Kyle.goyer@...>
Reply-To: <[email protected]>
Date: Saturday, May 30, 2020 at 9:17 AM
To: <[email protected]>
Subject: Re: [crestron] Best RGBWW controller for led light strip...

?

Crestron themselves have a couple controllers we like to use for LED Tape.?

Both wired and wireless
CLC-1LEDPWM-RGBW-EX
DIN-2LEDPWM8

if we need a deeper level of presets or show control we’ll put something like a Cueserver and DMX LED driver in line. Then just use the crestron to fire the scenes. ?


—碍测濒别