¿ªÔÆÌåÓý

ctrl + shift + ? for shortcuts
© 2025 Groups.io

Hubitat thermostat control


 

I'm trying to control some Ecobee stats using Jay's Hubitat module, I have feedback from the stats and control of the mode and fan. As of yet I can not change the setpoint. Does anyone know what the analog input is expecting?


 


Gary

I haven¡¯t personally had an ecobee to test with but if you send me a email I can work with you to figure out how to resolve the problem.?

Jay dot m dot basen at gmail?

Jay

On Thu, Mar 23, 2023 at 11:42 AM Gary Miller <g@...> wrote:
I'm trying to control some Ecobee stats using Jay's Hubitat module, I have feedback from the stats and control of the mode and fan. As of yet I can not change the setpoint. Does anyone know what the analog input is expecting?






 

¿ªÔÆÌåÓý

I figured it out, I was testing using the single setpoint input, and Ecobee doesn't support that. When I started using the heat and cool setpoint inputs it worked like a champ.

An analog increment limited to the range of the stat plus a delay on the send input did the trick. A two digit analog is what its looking for.

Thanks Jay, this works great.



On March 23, 2023 12:49:02 PM CDT, "jbasen via groups.io" <jay.m.basen@...> wrote:

Gary

I haven¡¯t personally had an ecobee to test with but if you send me a email I can work with you to figure out how to resolve the problem.?

Jay dot m dot basen at gmail?

Jay

On Thu, Mar 23, 2023 at 11:42 AM Gary Miller <g@...> wrote:
I'm trying to control some Ecobee stats using Jay's Hubitat module, I have feedback from the stats and control of the mode and fan. As of yet I can not change the setpoint. Does anyone know what the analog input is expecting?






 

I¡¯m glad it's working for you?

Thanks?

Jay

On Thu, Mar 23, 2023 at 5:30 PM Gary Miller <g@...> wrote:
I figured it out, I was testing using the single setpoint input, and Ecobee doesn't support that. When I started using the heat and cool setpoint inputs it worked like a champ.

An analog increment limited to the range of the stat plus a delay on the send input did the trick. A two digit analog is what its looking for.

Thanks Jay, this works great.



On March 23, 2023 12:49:02 PM CDT, "jbasen via " <jay.m.basen=[email protected]> wrote:

Gary

I haven¡¯t personally had an ecobee to test with but if you send me a email I can work with you to figure out how to resolve the problem.?

Jay dot m dot basen at gmail?

Jay

On Thu, Mar 23, 2023 at 11:42 AM Gary Miller <g@...> wrote:
I'm trying to control some Ecobee stats using Jay's Hubitat module, I have feedback from the stats and control of the mode and fan. As of yet I can not change the setpoint. Does anyone know what the analog input is expecting?