Veeder Root Control


 

Anyone ever control one of these??

?


 

I don't think you control them as much as just monitor them. We just did a slew of them on a data center project. I think by default they have an RS-232 port that is set up for modem dialing, you could probably find the protocol and just ignore the dialing strings.?

Or you can get a gateway that converts the RS-232 port to Modbus IP or BACnet IP. Our vendor used the Modbus IP gateway to connect to an electrical power monitoring system. With a BACnet/IP gateway you could probably just use the BACnet/IP functionality in a 3-series processor - free for 50 points but spend for that 51st point.

Usually there aren't a lot of parameters you need from this - tank level, tank low limit, tank high limit, tank overfill limit, maybe tank temperature and temp high limit. With BACnet you can just pick and choose which points to grab.

How may of these things you got?