Hi all
First time working with this processor. I am having trouble changing the output routing on this device. When the system first boots up I and change the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice versa. I am enabling the output in the module but it seems like that signal is staying high. Anyone have any ideas?
|
Have you turn system on on the module. Notjing can be done if the system is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@...> a crit :
toggle quoted message
Show quoted text
**
Hi all
First time working with this processor. I am having trouble changing the output routing on this device. When the system first boots up I and change the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice versa. I am enabling the output in the module but it seems like that signal is staying high. Anyone have any ideas?
|
Yes. That is the first thing I figured out.
toggle quoted message
Show quoted text
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@...> wrote: Have you turn system on on the module. Notjing can be done if the system is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@...> a écrit :
**
Hi all
First time working with this processor. I am having trouble changing the output routing on this device. When the system first boots up I and change the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice versa. I am enabling the output in the module but it seems like that signal is staying high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
How are you changing your routing value? I typically run through an init to change values.
toggle quoted message
Show quoted text
--- In Crestron@..., "lankford.patrick" <lankford.patrick@...> wrote: Yes. That is the first thing I figured out.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@> wrote:
Have you turn system on on the module. Notjing can be done if the system is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@> a écrit :
**
Hi all
First time working with this processor. I am having trouble changing the output routing on this device. When the system first boots up I and change the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice versa. I am enabling the output in the module but it seems like that signal is staying high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
Yes I am running them through an analog init before the go to the module. If I am reading this help file correct the Select_Video_x signal at the top of the module is selecting which output to send the input to? So I would need to send a 0 to that signal t0 clear the output to allow a new output to be selected?
toggle quoted message
Show quoted text
--- In Crestron@..., "Gregg M" <jets_in_2003@...> wrote: How are you changing your routing value? I typically run through an init to change values.
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@> wrote:
Have you turn system on on the module. Notjing can be done if the system is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@> a écrit :
**
Hi all
First time working with this processor. I am having trouble changing the output routing on this device. When the system first boots up I and change the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice versa. I am enabling the output in the module but it seems like that signal is staying high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
Each analog is an output, set the value to the input you want to route to that output.
toggle quoted message
Show quoted text
--- In Crestron@..., "lankford.patrick" <lankford.patrick@...> wrote: Yes I am running them through an analog init before the go to the module. If I am reading this help file correct the Select_Video_x signal at the top of the module is selecting which output to send the input to? So I would need to send a 0 to that signal t0 clear the output to allow a new output to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
How are you changing your routing value? I typically run through an init to change values.
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@> wrote:
Have you turn system on on the module. Notjing can be done if the system is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@> a écrit :
**
Hi all
First time working with this processor. I am having trouble changing the output routing on this device. When the system first boots up I and change the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice versa. I am enabling the output in the module but it seems like that signal is staying high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
If you do the routing from the front panel of the dmps does it work? If you want to sent the input 1 of the dmps to the output 1, you set 1d to the video 1 output (hdmi). On the left side of the system symbol. The right side provide you the actual value of that output, by changing the routing from the front panel, that value is supposed to change. {Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@...> a crit : **
Yes I am running them through an analog init before the go to the module. If I am reading this help file correct the Select_Video_x signal at the top of the module is selecting which output to send the input to? So I would need to send a 0 to that signal t0 clear the output to allow a new output to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@...> wrote:
How are you changing your routing value? I typically run through an init to change values.
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., Raphal Thiffault <raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be done if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@> a crit :
**
Hi all
First time working with this processor. I am having trouble
changing the
output routing on this device. When the system first boots up I
and change
the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice
versa. I am
enabling the output in the module but it seems like that signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
|
Yes. I can route just fine from the front panel. I have inputs going into analog init with values set for 1d, 2d, 3d and so forth. Those then go to outputs in the module for video HDMI out 1 and 2 and another analog init for DM out as well. When output is selected I can switch the inputs from the program in the touch panel and all is good. But when I change sources to send inputs to DM out 3 the switching does not occur. As soon as I route outputs again from the front panel I can switch all over again.
toggle quoted message
Show quoted text
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@...> wrote: If you do the routing from the front panel of the dmps does it work?
If you want to sent the input 1 of the dmps to the output 1, you set 1d to the video 1 output (hdmi). On the left side of the system symbol. The right side provide you the actual value of that output, by changing the routing from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@...> a écrit :
**
Yes I am running them through an analog init before the go to the module. If I am reading this help file correct the Select_Video_x signal at the top of the module is selecting which output to send the input to? So I would need to send a 0 to that signal t0 clear the output to allow a new output to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
How are you changing your routing value? I typically run through an init to change values.
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be done if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@> a écrit :
**
Hi all
First time working with this processor. I am having trouble
changing the
output routing on this device. When the system first boots up I
and change
the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice
versa. I am
enabling the output in the module but it seems like that signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
When you route signal to the DM out does the FB correspond to the value being sent? Also if you are running seperate inits for all your outputs you can route a working one (HDMI out 1 or 2) to the DM out to test whether its a code mistake. Finally in debugger just change the value of that Select_Video_DM_Out_3 line and see if the source changes on your display
toggle quoted message
Show quoted text
--- In Crestron@..., "lankford.patrick" <lankford.patrick@...> wrote: Yes. I can route just fine from the front panel. I have inputs going into analog init with values set for 1d, 2d, 3d and so forth. Those then go to outputs in the module for video HDMI out 1 and 2 and another analog init for DM out as well. When output is selected I can switch the inputs from the program in the touch panel and all is good. But when I change sources to send inputs to DM out 3 the switching does not occur. As soon as I route outputs again from the front panel I can switch all over again.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@> wrote:
If you do the routing from the front panel of the dmps does it work?
If you want to sent the input 1 of the dmps to the output 1, you set 1d to the video 1 output (hdmi). On the left side of the system symbol. The right side provide you the actual value of that output, by changing the routing from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@> a écrit :
**
Yes I am running them through an analog init before the go to the module. If I am reading this help file correct the Select_Video_x signal at the top of the module is selecting which output to send the input to? So I would need to send a 0 to that signal t0 clear the output to allow a new output to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
How are you changing your routing value? I typically run through an init to change values.
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be done if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@> a écrit :
**
Hi all
First time working with this processor. I am having trouble
changing the
output routing on this device. When the system first boots up I
and change
the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice
versa. I am
enabling the output in the module but it seems like that signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
I have done many of these systems, and I can tell you the way I deal with it...
Button press 1-6 (inputs)
to Interlock 1-6 to 1-6fb
1-6fb to Analog Initialize 0-6d to Select Video HDMI Out 1, Select Video HDMI Out 2, Select Video DM Out 3, and Select Video DM Out 4 on the Module.
I do the same for Audio matching the inputs of the video.
I have a Power button that clears the interlock as well asn video and audio.
Hope this helps
toggle quoted message
Show quoted text
--- In Crestron@..., "Gregg M" <jets_in_2003@...> wrote: When you route signal to the DM out does the FB correspond to the value being sent? Also if you are running seperate inits for all your outputs you can route a working one (HDMI out 1 or 2) to the DM out to test whether its a code mistake. Finally in debugger just change the value of that Select_Video_DM_Out_3 line and see if the source changes on your display
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. I can route just fine from the front panel. I have inputs going into analog init with values set for 1d, 2d, 3d and so forth. Those then go to outputs in the module for video HDMI out 1 and 2 and another analog init for DM out as well. When output is selected I can switch the inputs from the program in the touch panel and all is good. But when I change sources to send inputs to DM out 3 the switching does not occur. As soon as I route outputs again from the front panel I can switch all over again.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@> wrote:
If you do the routing from the front panel of the dmps does it work?
If you want to sent the input 1 of the dmps to the output 1, you set 1d to the video 1 output (hdmi). On the left side of the system symbol. The right side provide you the actual value of that output, by changing the routing from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@> a écrit :
**
Yes I am running them through an analog init before the go to the module. If I am reading this help file correct the Select_Video_x signal at the top of the module is selecting which output to send the input to? So I would need to send a 0 to that signal t0 clear the output to allow a new output to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
How are you changing your routing value? I typically run through an init to change values.
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be done if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@> a écrit :
**
Hi all
First time working with this processor. I am having trouble
changing the
output routing on this device. When the system first boots up I
and change
the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice
versa. I am
enabling the output in the module but it seems like that signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
Why use an IL and an INIT? Why not feed the INIT with the button press, and EQU the DMPS output FB for your button feedback? On Thu, Mar 28, 2013 at 11:42 AM, <cochoa2716@...> wrote: **
I have done many of these systems, and I can tell you the way I deal with it...
Button press 1-6 (inputs)
to Interlock 1-6 to 1-6fb
1-6fb to Analog Initialize 0-6d to Select Video HDMI Out 1, Select Video HDMI Out 2, Select Video DM Out 3, and Select Video DM Out 4 on the Module.
I do the same for Audio matching the inputs of the video.
I have a Power button that clears the interlock as well asn video and audio.
Hope this helps
--- In Crestron@..., "Gregg M" <jets_in_2003@...> wrote:
When you route signal to the DM out does the FB correspond to the value being sent?
Also if you are running seperate inits for all your outputs you can route a working one (HDMI out 1 or 2) to the DM out to test whether its a code mistake.
Finally in debugger just change the value of that Select_Video_DM_Out_3 line and see if the source changes on your display
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. I can route just fine from the front panel. I have inputs going
into analog init with values set for 1d, 2d, 3d and so forth. Those then go to outputs in the module for video HDMI out 1 and 2 and another analog init for DM out as well. When output is selected I can switch the inputs from the program in the touch panel and all is good. But when I change sources to send inputs to DM out 3 the switching does not occur. As soon as I route outputs again from the front panel I can switch all over again.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@>
wrote:
If you do the routing from the front panel of the dmps does it work?
If you want to sent the input 1 of the dmps to the output 1, you set
1d to
the video 1 output (hdmi). On the left side of the system symbol.
The right
side provide you the actual value of that output, by changing the
routing
from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@> a écrit :
**
Yes I am running them through an analog init before the go to the
module.
If I am reading this help file correct the Select_Video_x signal
at the top
of the module is selecting which output to send the input to? So I
would
need to send a 0 to that signal t0 clear the output to allow a new
output
to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
How are you changing your routing value? I typically run through
an init
to change values.
--- In Crestron@..., "lankford.patrick"
<lankford.patrick@>
wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., 鲹ë Thiffault
<raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be done
if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@>
a
écrit :
**
Hi all
First time working with this processor. I am having trouble
changing the
output routing on this device. When the system first boots
up I
and change
the output routing to output 2 or 3. But if i change in to
output 2
initially I cannot then switch to route to output 3 and
vice
versa. I am
enabling the output in the module but it seems like that
signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
Well as a wise man once said.. "to each his own..." I find it easier to use an interlock and I was just sharing the way I do it. If you have a suggestion for him, maybe let him know..
EQU would require more steps than just using the IL.
toggle quoted message
Show quoted text
--- In Crestron@..., Phil Bridges <gravityhammer@...> wrote: Why use an IL and an INIT? Why not feed the INIT with the button press, and EQU the DMPS output FB for your button feedback?
On Thu, Mar 28, 2013 at 11:42 AM, <cochoa2716@...> wrote:
**
I have done many of these systems, and I can tell you the way I deal with it...
Button press 1-6 (inputs)
to Interlock 1-6 to 1-6fb
1-6fb to Analog Initialize 0-6d to Select Video HDMI Out 1, Select Video HDMI Out 2, Select Video DM Out 3, and Select Video DM Out 4 on the Module.
I do the same for Audio matching the inputs of the video.
I have a Power button that clears the interlock as well asn video and audio.
Hope this helps
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
When you route signal to the DM out does the FB correspond to the value being sent?
Also if you are running seperate inits for all your outputs you can route a working one (HDMI out 1 or 2) to the DM out to test whether its a code mistake.
Finally in debugger just change the value of that Select_Video_DM_Out_3 line and see if the source changes on your display
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. I can route just fine from the front panel. I have inputs going
into analog init with values set for 1d, 2d, 3d and so forth. Those then go to outputs in the module for video HDMI out 1 and 2 and another analog init for DM out as well. When output is selected I can switch the inputs from the program in the touch panel and all is good. But when I change sources to send inputs to DM out 3 the switching does not occur. As soon as I route outputs again from the front panel I can switch all over again.
--- In Crestron@..., Raphaël Thiffault <raphaelthiffault@>
wrote:
If you do the routing from the front panel of the dmps does it work?
If you want to sent the input 1 of the dmps to the output 1, you set
1d to
the video 1 output (hdmi). On the left side of the system symbol.
The right
side provide you the actual value of that output, by changing the
routing
from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@> a écrit :
**
Yes I am running them through an analog init before the go to the
module.
If I am reading this help file correct the Select_Video_x signal
at the top
of the module is selecting which output to send the input to? So I
would
need to send a 0 to that signal t0 clear the output to allow a new
output
to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
How are you changing your routing value? I typically run through
an init
to change values.
--- In Crestron@..., "lankford.patrick"
<lankford.patrick@>
wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., Raphaël Thiffault
<raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be done
if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@>
a
écrit :
**
Hi all
First time working with this processor. I am having trouble
changing the
output routing on this device. When the system first boots
up I
and change
the output routing to output 2 or 3. But if i change in to
output 2
initially I cannot then switch to route to output 3 and
vice
versa. I am
enabling the output in the module but it seems like that
signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
|
It would, until you need feedback from the device. In addition, INIT/EQUs are *much* more flexible than ILs - especially when you have multiple things that can trigger the value. On Thu, Mar 28, 2013 at 11:53 AM, <cochoa2716@...> wrote: **
Well as a wise man once said.. "to each his own..." I find it easier to use an interlock and I was just sharing the way I do it. If you have a suggestion for him, maybe let him know..
EQU would require more steps than just using the IL.
--- In Crestron@..., Phil Bridges <gravityhammer@...> wrote:
Why use an IL and an INIT? Why not feed the INIT with the button press, and EQU the DMPS output FB for your button feedback?
On Thu, Mar 28, 2013 at 11:42 AM, <cochoa2716@...> wrote:
**
I have done many of these systems, and I can tell you the way I deal
with
it...
Button press 1-6 (inputs)
to Interlock 1-6 to 1-6fb
1-6fb to Analog Initialize 0-6d to Select Video HDMI Out 1, Select Video
HDMI Out 2, Select Video DM Out 3, and Select Video DM Out 4 on the Module.
I do the same for Audio matching the inputs of the video.
I have a Power button that clears the interlock as well asn video and audio.
Hope this helps
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
When you route signal to the DM out does the FB correspond to the
value
being sent?
Also if you are running seperate inits for all your outputs you can route a working one (HDMI out 1 or 2) to the DM out to test whether its a
code mistake.
Finally in debugger just change the value of that Select_Video_DM_Out_3
line and see if the source changes on your display
--- In Crestron@..., "lankford.patrick"
<lankford.patrick@>
wrote:
Yes. I can route just fine from the front panel. I have inputs
going
into analog init with values set for 1d, 2d, 3d and so forth. Those then go
to outputs in the module for video HDMI out 1 and 2 and another analog init
for DM out as well. When output is selected I can switch the inputs from
the program in the touch panel and all is good. But when I change sources
to send inputs to DM out 3 the switching does not occur. As soon as I route
outputs again from the front panel I can switch all over again.
--- In Crestron@..., Raphaël Thiffault
<raphaelthiffault@>
wrote:
If you do the routing from the front panel of the dmps does it
work?
If you want to sent the input 1 of the dmps to the output 1, you
set
1d to
the video 1 output (hdmi). On the left side of the system symbol.
The right
side provide you the actual value of that output, by changing the
routing
from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@> a écrit :
**
Yes I am running them through an analog init before the go to
the
module.
If I am reading this help file correct the Select_Video_x
signal
at the top
of the module is selecting which output to send the input to?
So I
would
need to send a 0 to that signal t0 clear the output to allow a
new
output
to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@>
wrote:
How are you changing your routing value? I typically run
through
an init
to change values.
--- In Crestron@..., "lankford.patrick"
<lankford.patrick@>
wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., Raphaël Thiffault
<raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be
done
if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick"
<lankford.patrick@>
a
écrit :
**
Hi all
First time working with this processor. I am having
trouble
changing the
output routing on this device. When the system first
boots
up I
and change
the output routing to output 2 or 3. But if i change
in to
output 2
initially I cannot then switch to route to output 3 and
vice
versa. I am
enabling the output in the module but it seems like
that
signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
|
I'm with Phil on this one. I haven't used an interlock symbol in years... On 2013-03-28, at 9:55 AM, Phil Bridges <gravityhammer@...> wrote: It would, until you need feedback from the device. In addition, INIT/EQUs are *much* more flexible than ILs - especially when you have multiple things that can trigger the value.
On Thu, Mar 28, 2013 at 11:53 AM, <cochoa2716@...> wrote:
**
Well as a wise man once said.. "to each his own..." I find it easier to use an interlock and I was just sharing the way I do it. If you have a suggestion for him, maybe let him know..
EQU would require more steps than just using the IL.
--- In Crestron@..., Phil Bridges <gravityhammer@...> wrote:
Why use an IL and an INIT? Why not feed the INIT with the button press, and EQU the DMPS output FB for your button feedback?
On Thu, Mar 28, 2013 at 11:42 AM, <cochoa2716@...> wrote:
**
I have done many of these systems, and I can tell you the way I deal
with
it...
Button press 1-6 (inputs)
to Interlock 1-6 to 1-6fb
1-6fb to Analog Initialize 0-6d to Select Video HDMI Out 1, Select Video
HDMI Out 2, Select Video DM Out 3, and Select Video DM Out 4 on the Module.
I do the same for Audio matching the inputs of the video.
I have a Power button that clears the interlock as well asn video and audio.
Hope this helps
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
When you route signal to the DM out does the FB correspond to the
value
being sent?
Also if you are running seperate inits for all your outputs you can route a working one (HDMI out 1 or 2) to the DM out to test whether its a
code mistake.
Finally in debugger just change the value of that Select_Video_DM_Out_3
line and see if the source changes on your display
--- In Crestron@..., "lankford.patrick"
<lankford.patrick@>
wrote:
Yes. I can route just fine from the front panel. I have inputs
going
into analog init with values set for 1d, 2d, 3d and so forth. Those then go
to outputs in the module for video HDMI out 1 and 2 and another analog init
for DM out as well. When output is selected I can switch the inputs from
the program in the touch panel and all is good. But when I change sources
to send inputs to DM out 3 the switching does not occur. As soon as I route
outputs again from the front panel I can switch all over again.
--- In Crestron@..., Raphaël Thiffault
<raphaelthiffault@>
wrote:
If you do the routing from the front panel of the dmps does it
work?
If you want to sent the input 1 of the dmps to the output 1, you
set
1d to
the video 1 output (hdmi). On the left side of the system symbol.
The right
side provide you the actual value of that output, by changing the
routing
from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@> a écrit :
**
Yes I am running them through an analog init before the go to
the
module.
If I am reading this help file correct the Select_Video_x
signal
at the top
of the module is selecting which output to send the input to?
So I
would
need to send a 0 to that signal t0 clear the output to allow a
new
output
to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@>
wrote:
How are you changing your routing value? I typically run
through
an init
to change values.
--- In Crestron@..., "lankford.patrick"
<lankford.patrick@>
wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., Raphaël Thiffault
<raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be
done
if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick"
<lankford.patrick@>
a
écrit :
**
Hi all
First time working with this processor. I am having
trouble
changing the
output routing on this device. When the system first
boots
up I
and change
the output routing to output 2 or 3. But if i change
in to
output 2
initially I cannot then switch to route to output 3 and
vice
versa. I am
enabling the output in the module but it seems like
that
signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
Reply via web post Reply to sender Reply to group Start a New Topic Messages in this topic (13) RECENT ACTIVITY: New Members 87 New Files 7 Visit Your Group
Check out the Files area for useful modules, documents, and drivers.
A contact list of Crestron dealers and programmers can be found in the Database area.
[Non-text portions of this message have been removed]
|
Here's the way a connect to the System Control Module.
It's a screen shot of a dmps200 but it's the same.
toggle quoted message
Show quoted text
--- In Crestron@..., "lankford.patrick" <lankford.patrick@...> wrote: Yes. I can route just fine from the front panel. I have inputs going into analog init with values set for 1d, 2d, 3d and so forth. Those then go to outputs in the module for video HDMI out 1 and 2 and another analog init for DM out as well. When output is selected I can switch the inputs from the program in the touch panel and all is good. But when I change sources to send inputs to DM out 3 the switching does not occur. As soon as I route outputs again from the front panel I can switch all over again.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@> wrote:
If you do the routing from the front panel of the dmps does it work?
If you want to sent the input 1 of the dmps to the output 1, you set 1d to the video 1 output (hdmi). On the left side of the system symbol. The right side provide you the actual value of that output, by changing the routing from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@> a écrit :
**
Yes I am running them through an analog init before the go to the module. If I am reading this help file correct the Select_Video_x signal at the top of the module is selecting which output to send the input to? So I would need to send a 0 to that signal t0 clear the output to allow a new output to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
How are you changing your routing value? I typically run through an init to change values.
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., 鲹ë Thiffault <raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be done if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@> a écrit :
**
Hi all
First time working with this processor. I am having trouble
changing the
output routing on this device. When the system first boots up I
and change
the output routing to output 2 or 3. But if i change in to output 2 initially I cannot then switch to route to output 3 and vice
versa. I am
enabling the output in the module but it seems like that signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
|
Hey guys thanks for all the help. Looks like it wasn't a programming error. Got off the phone with True Blue and I guess the routing fb on the front panel is OOTBF. To show this fb in the program I would need to use serial codes for the fb (least of my worries at this point). Ended up hooking some displays up and routing was taking place it just wants giving fb on the front panel.
Thanks!!
toggle quoted message
Show quoted text
--- In Crestron@..., Phil Bridges <gravityhammer@...> wrote: Why use an IL and an INIT? Why not feed the INIT with the button press, and EQU the DMPS output FB for your button feedback?
On Thu, Mar 28, 2013 at 11:42 AM, <cochoa2716@...> wrote:
**
I have done many of these systems, and I can tell you the way I deal with it...
Button press 1-6 (inputs)
to Interlock 1-6 to 1-6fb
1-6fb to Analog Initialize 0-6d to Select Video HDMI Out 1, Select Video HDMI Out 2, Select Video DM Out 3, and Select Video DM Out 4 on the Module.
I do the same for Audio matching the inputs of the video.
I have a Power button that clears the interlock as well asn video and audio.
Hope this helps
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
When you route signal to the DM out does the FB correspond to the value being sent?
Also if you are running seperate inits for all your outputs you can route a working one (HDMI out 1 or 2) to the DM out to test whether its a code mistake.
Finally in debugger just change the value of that Select_Video_DM_Out_3 line and see if the source changes on your display
--- In Crestron@..., "lankford.patrick" <lankford.patrick@> wrote:
Yes. I can route just fine from the front panel. I have inputs going
into analog init with values set for 1d, 2d, 3d and so forth. Those then go to outputs in the module for video HDMI out 1 and 2 and another analog init for DM out as well. When output is selected I can switch the inputs from the program in the touch panel and all is good. But when I change sources to send inputs to DM out 3 the switching does not occur. As soon as I route outputs again from the front panel I can switch all over again.
--- In Crestron@..., Raphaël Thiffault <raphaelthiffault@>
wrote:
If you do the routing from the front panel of the dmps does it work?
If you want to sent the input 1 of the dmps to the output 1, you set
1d to
the video 1 output (hdmi). On the left side of the system symbol.
The right
side provide you the actual value of that output, by changing the
routing
from the front panel, that value is supposed to change.
{Paf} Le 27 mars 2013 22:00, "lankford.patrick" <lankford.patrick@> a écrit :
**
Yes I am running them through an analog init before the go to the
module.
If I am reading this help file correct the Select_Video_x signal
at the top
of the module is selecting which output to send the input to? So I
would
need to send a 0 to that signal t0 clear the output to allow a new
output
to be selected?
--- In Crestron@..., "Gregg M" <jets_in_2003@> wrote:
How are you changing your routing value? I typically run through
an init
to change values.
--- In Crestron@..., "lankford.patrick"
<lankford.patrick@>
wrote:
Yes. That is the first thing I figured out.
--- In Crestron@..., Raphaël Thiffault
<raphaelthiffault@>
wrote:
Have you turn system on on the module. Notjing can be done
if the
system
is not on.
{Paf} Le 27 mars 2013 19:48, "lankford.patrick" <lankford.patrick@>
a
écrit :
**
Hi all
First time working with this processor. I am having trouble
changing the
output routing on this device. When the system first boots
up I
and change
the output routing to output 2 or 3. But if i change in to
output 2
initially I cannot then switch to route to output 3 and
vice
versa. I am
enabling the output in the module but it seems like that
signal is
staying
high. Anyone have any ideas?
[Non-text portions of this message have been removed]
[Non-text portions of this message have been removed]
|
Type in a number, select the fields below it, hit F4.
Yeah, to each their own, but those extra steps seem very worth it to me...
- Chip
toggle quoted message
Show quoted text
--- In Crestron@..., cochoa2716@... wrote:
EQU would require more steps than just using the IL.
|