Figured I would bump this one.
We have (12) units on this project and every single one was getting wild temperature readings from both the internal and remote sensors.? Upgraded to 1.1.43.1 firmware, connected via Thermostat tool and set all thermostats to Remote Sensor 1 Space, all others Ommitted.? Made various other settings such as deadbands, dual auto setpoints and sent configuration to devices.? Fwiw, you need to manually accept the configurations when they are sent to the thermostat as well via on screen notification, fun.
Seems to have corrected the wild swings and error messages for the moment.? Will report back if that changes, but this sequence seems to address the issue.
Side note, for Josh.ai integrators, the HZ-THSTAT obviously does not have a 1pt_Auto_Setpoint_FB signal, so you will need to use a not on the Dual_Setpoint_FB signal.? You will also need to run your Mode_Fb into an SIO with "heat" "cool" "auto" for the output into the Josh.ai Climate module.??
toggle quoted message
Show quoted text
On Thu, Apr 7, 2022 at 02:46 PM, ckangis wrote:
Has anyone actually installed any of these recently??? (I know, I know...has anyone actually received any of these recently???)
If so, Has the issue with unreliable room temp readings been resolved yet??