I notice that "index pulse" can be checked on the parallel input to
pick up the true speed of a machine. Can the PWM frequency of a VFD
be used for this? If so, can it be scaled in MACH2 to correspnd to
the speed (I believe speed is a linear function to frequency, but the
numeric value of one will not be the same as the other.

Jeff


 

Not enough precision for threading. Even if you could do a PWM to pulse
convertor it will not work. You will need a true encoder, home made or not.
More, it will be simpler.

For threading you don't only need the exact speed of the spindle, but his
absolute position too with a good accuracy. Can only be done with an encoder
with index + eventually other pulses for low or medium speed applications.

Olivier.


washcomp
 

Olivier:

Actually, this question revolved around my Bridgeport mill. In this
case I'd like to get "feedback" to MACH2 and to a readout of RPM, but
I don't think the number is as critical as in a lathe. I just
thought it made sense to use the pulses from the VFD to drive the
readout. An error of a percent or two probably wouldn't matter for
this application. It's just that the number of pulses would have to
be able to be scaled to make the read out make sense in RPM. Is
there a way to scale in MACH2 between the pulses and the RPM?

Jeff

--- In mach1mach2cnc@..., "Digital audio Pro"
<digitalaudiopro@w...> wrote:
Not enough precision for threading. Even if you could do a PWM to
pulse
convertor it will not work. You will need a true encoder, home made
or not.
More, it will be simpler.

For threading you don't only need the exact speed of the spindle,
but his
absolute position too with a good accuracy. Can only be done with
an encoder
with index + eventually other pulses for low or medium speed
applications.

Olivier.



 

don't think. Art and others will confirm. But a PWM signal is not a pulse
signal. it will be complicated to convert it. Mach2 accept only index
pulses.



Olivier.


Art
 

Jeff:

the read out make sense in RPM. Is
there a way to scale in MACH2 between the pulses and the RPM?


YEs, Mach2 will scale the input automatically and display RPM. I believe
even Mill can do this as long as the index or timing mark inputs are hooked
up and activated. Have you hooked them up yet??

Thanks,
Art
www.artofcnc.ca

----- Original Message -----
From: "washcomp" <jeff@...>
To: <mach1mach2cnc@...>
Sent: Monday, March 01, 2004 10:32 AM
Subject: [mach1mach2cnc] Re: Question on index pulse


Olivier:

Actually, this question revolved around my Bridgeport mill. In this
case I'd like to get "feedback" to MACH2 and to a readout of RPM, but
I don't think the number is as critical as in a lathe. I just
thought it made sense to use the pulses from the VFD to drive the
readout. An error of a percent or two probably wouldn't matter for
this application. It's just that the number of pulses would have to
be able to be scaled to make the read out make sense in RPM. Is
there a way to scale in MACH2 between the pulses and the RPM?

Jeff

--- In mach1mach2cnc@..., "Digital audio Pro"
<digitalaudiopro@w...> wrote:
Not enough precision for threading. Even if you could do a PWM to
pulse
convertor it will not work. You will need a true encoder, home made
or not.
More, it will be simpler.

For threading you don't only need the exact speed of the spindle,
but his
absolute position too with a good accuracy. Can only be done with
an encoder
with index + eventually other pulses for low or medium speed
applications.

Olivier.





Yahoo! Groups Links





Andy Wander
 

Of course, VFD means Variable Frequency, so is this actually a PWM signal?
I'm so confused...

Andy Wander
Verrex Corporation

-----Original Message-----
From: washcomp [mailto:jeff@...]
Sent: Monday, March 01, 2004 8:42 AM
To: mach1mach2cnc@...
Subject: [mach1mach2cnc] Question on index pulse

I notice that "index pulse" can be checked on the parallel input to
pick up the true speed of a machine. Can the PWM frequency of a VFD
be used for this? If so, can it be scaled in MACH2 to correspnd to
the speed (I believe speed is a linear function to frequency, but the
numeric value of one will not be the same as the other.

Jeff





Yahoo! Groups Sponsor


ADVERTISEMENT


Click HereClick Here


<
/S=:HM/A=2019528/rand=446470174>

_____

Yahoo! Groups Links
* To visit your group on the web, go to:

<>

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms of
<> Service.


washcomp
 

Unless I'm mistaken, (wouldn't be the first time), the way the
frequency variation manifests itself is by modulating the pulse
width. Pulses shorter and closer together = higher frequency.

Please correct me if I'm wrong.

Jeff

--- In mach1mach2cnc@..., Andy Wander <awander@v...>
wrote:
Of course, VFD means Variable Frequency, so is this actually a PWM
signal?
I'm so confused...

Andy Wander
Verrex Corporation

-----Original Message-----
From: washcomp [mailto:jeff@w...]
Sent: Monday, March 01, 2004 8:42 AM
To: mach1mach2cnc@...
Subject: [mach1mach2cnc] Question on index pulse

I notice that "index pulse" can be checked on the parallel input to
pick up the true speed of a machine. Can the PWM frequency of a
VFD
be used for this? If so, can it be scaled in MACH2 to correspnd to
the speed (I believe speed is a linear function to frequency, but
the
numeric value of one will not be the same as the other.

Jeff





Yahoo! Groups Sponsor


ADVERTISEMENT


Click HereClick Here


<
M=274551.4550177.5761904.1261774/D=egroupweb
/S=:HM/A=2019528/rand=446470174>

_____

Yahoo! Groups Links
* To visit your group on the web, go to:

<>

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?
subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms
of
<> Service.



 

No, it is the same base frequency. The width of the pulse ( length of time
it is high ) determines the energy it can deliver. 80% PWM = 80% of the time
it high and 20% is low.
Jim

----- Original Message -----
From: "washcomp" <jeff@...>
To: <mach1mach2cnc@...>
Sent: Monday, March 01, 2004 11:36 AM
Subject: [mach1mach2cnc] Re: Question on index pulse


Unless I'm mistaken, (wouldn't be the first time), the way the
frequency variation manifests itself is by modulating the pulse
width. Pulses shorter and closer together = higher frequency.

Please correct me if I'm wrong.

Jeff

--- In mach1mach2cnc@..., Andy Wander <awander@v...>
wrote:
Of course, VFD means Variable Frequency, so is this actually a PWM
signal?
I'm so confused...

Andy Wander
Verrex Corporation

-----Original Message-----
From: washcomp [mailto:jeff@w...]
Sent: Monday, March 01, 2004 8:42 AM
To: mach1mach2cnc@...
Subject: [mach1mach2cnc] Question on index pulse

I notice that "index pulse" can be checked on the parallel input to
pick up the true speed of a machine. Can the PWM frequency of a
VFD
be used for this? If so, can it be scaled in MACH2 to correspnd to
the speed (I believe speed is a linear function to frequency, but
the
numeric value of one will not be the same as the other.

Jeff





Yahoo! Groups Sponsor


ADVERTISEMENT


Click HereClick Here


<
M=274551.4550177.5761904.1261774/D=egroupweb
/S=:HM/A=2019528/rand=446470174>

_____

Yahoo! Groups Links
* To visit your group on the web, go to:

<>

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?
subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms
of
<> Service.





Yahoo! Groups Links




Andy Wander
 

I can't speak about the intricacies of the VFD, but PWM is Pulse Width
Modulation, where the ONLY thing that is varied is the width of the "ON"
pulse(not both ON and OFF). This means that the frequency of the pulses does
NOT change, just the ratio of ON-time to OFF time of a (quasi) square wave.

If the width of both the ON and the OFF pulse changed(and was identical, you
would NOT have PWM, you would have FM(frequency modulation) of a square
wave.

Andy Wander
Verrex Corporation

-----Original Message-----
From: washcomp [mailto:jeff@...]
Sent: Monday, March 01, 2004 12:36 PM
To: mach1mach2cnc@...
Subject: [mach1mach2cnc] Re: Question on index pulse

Unless I'm mistaken, (wouldn't be the first time), the way the
frequency variation manifests itself is by modulating the pulse
width. Pulses shorter and closer together = higher frequency.

Please correct me if I'm wrong.

Jeff

--- In mach1mach2cnc@..., Andy Wander <awander@v...>
wrote:
Of course, VFD means Variable Frequency, so is this actually a PWM
signal?
I'm so confused...

Andy Wander
Verrex Corporation

-----Original Message-----
From: washcomp [mailto:jeff@w...]
Sent: Monday, March 01, 2004 8:42 AM
To: mach1mach2cnc@...
Subject: [mach1mach2cnc] Question on index pulse

I notice that "index pulse" can be checked on the parallel input to
pick up the true speed of a machine. Can the PWM frequency of a
VFD
be used for this? If so, can it be scaled in MACH2 to correspnd to
the speed (I believe speed is a linear function to frequency, but
the
numeric value of one will not be the same as the other.

Jeff





Yahoo! Groups Sponsor


ADVERTISEMENT


Click HereClick Here


< <>
M=274551.4550177.5761904.1261774/D=egroupweb
/S=:HM/A=2019528/rand=446470174>

_____

Yahoo! Groups Links
* To visit your group on the web, go to:
<>
<
<> >

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?
subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms
of
< <> >
Service.




_____

Yahoo! Groups Links
* To visit your group on the web, go to:

<>

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms of
<> Service.


Andy Wander
 

Of course, by changing the width of the ON pulkse, while the frequency stays
the same, the width of the OFF pulse is changed also, in the opposite
direction.

For example a 50% PWM pulse train will look just like a square wave at that
frequency, because the ON pulse will be 50" of the period, and so will the
OFF pulse.

A 20% PWM will have the ON time at 20" of the period, and the OFF at 80%.

Etc..

Andy Wander
Verrex Corporation

-----Original Message-----
From: Andy Wander [mailto:awander@...]
Sent: Monday, March 01, 2004 12:40 PM
To: 'mach1mach2cnc@...'
Subject: RE: [mach1mach2cnc] Re: Question on index pulse

I can't speak about the intricacies of the VFD, but PWM is Pulse Width
Modulation, where the ONLY thing that is varied is the width of the "ON"
pulse(not both ON and OFF). This means that the frequency of the pulses does
NOT change, just the ratio of ON-time to OFF time of a (quasi) square wave.

If the width of both the ON and the OFF pulse changed(and was identical, you
would NOT have PWM, you would have FM(frequency modulation) of a square
wave.

Andy Wander
Verrex Corporation

-----Original Message-----
From: washcomp [mailto:jeff@...]
Sent: Monday, March 01, 2004 12:36 PM
To: mach1mach2cnc@...
Subject: [mach1mach2cnc] Re: Question on index pulse

Unless I'm mistaken, (wouldn't be the first time), the way the
frequency variation manifests itself is by modulating the pulse
width. Pulses shorter and closer together = higher frequency.

Please correct me if I'm wrong.

Jeff

--- In mach1mach2cnc@..., Andy Wander <awander@v...>
wrote:
Of course, VFD means Variable Frequency, so is this actually a PWM
signal?
I'm so confused...

Andy Wander
Verrex Corporation

-----Original Message-----
From: washcomp [mailto:jeff@w...]
Sent: Monday, March 01, 2004 8:42 AM
To: mach1mach2cnc@...
Subject: [mach1mach2cnc] Question on index pulse

I notice that "index pulse" can be checked on the parallel input to
pick up the true speed of a machine. Can the PWM frequency of a
VFD
be used for this? If so, can it be scaled in MACH2 to correspnd to
the speed (I believe speed is a linear function to frequency, but
the
numeric value of one will not be the same as the other.

Jeff





Yahoo! Groups Sponsor


ADVERTISEMENT


Click HereClick Here


< <> <
<> >
M=274551.4550177.5761904.1261774/D=egroupweb
/S=:HM/A=2019528/rand=446470174>

_____

Yahoo! Groups Links
* To visit your group on the web, go to:
<>
<
<> >
<
<>
<
<> > >

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?
subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms
of
< <> <
<> > >
Service.




_____

Yahoo! Groups Links
* To visit your group on the web, go to:

<>
<
<> >

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms of
< <> >
Service.








Yahoo! Groups Sponsor


ADVERTISEMENT


Click HereClick Here


<
/S=:HM/A=2019528/rand=704545992>

_____

Yahoo! Groups Links
* To visit your group on the web, go to:

<>

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms of
<> Service.


Les Newell
 

A VFD creates an approximation of a sine wave by pulse width modulating a high frequency carrier. The carrier frequency is high enough that the motor effecively filters it out, leaving the sine wave. The frequency of the sine wave is varied to control the speed of the motor.

This is not really much use to Mach2 as it is only the commanded speed to the motor. It does not mean the motor will actually turn at that speed. The best thing to do is fit a sensor on the spindle and have done with it. That way Mach2 always knows the true speed of the spindle.

Les


Andy Wander wrote:

I can't speak about the intricacies of the VFD, but PWM is Pulse Width
Modulation, where the ONLY thing that is varied is the width of the "ON"
pulse(not both ON and OFF). This means that the frequency of the pulses does
NOT change, just the ratio of ON-time to OFF time of a (quasi) square wave.
If the width of both the ON and the OFF pulse changed(and was identical, you
would NOT have PWM, you would have FM(frequency modulation) of a square
wave. Andy Wander
Verrex Corporation


Andy Wander
 

Les:

Thanks for the explanation-what I still don't understand about it is how the
"Sine Wave", which is generated by the "filtering" of the motor, will vary
in frequency, if the only thing that is done to it is to change the PWM duty
cycle. This would seem to me to get us to a "Sine wave" which has different
values for it's Positive and Negative half-cycles, but I can't see how the
frequency would change unless the frequency of the PWM changed.


Andy Wander
Verrex Corporation

-----Original Message-----
From: Les Newell [mailto:les@...]
Sent: Monday, March 01, 2004 12:54 PM
To: mach1mach2cnc@...
Subject: Re: [mach1mach2cnc] Re: Question on index pulse

A VFD creates an approximation of a sine wave by pulse width modulating
a high frequency carrier. The carrier frequency is high enough that the
motor effecively filters it out, leaving the sine wave. The frequency of
the sine wave is varied to control the speed of the motor.

This is not really much use to Mach2 as it is only the commanded speed
to the motor. It does not mean the motor will actually turn at that
speed. The best thing to do is fit a sensor on the spindle and have done
with it. That way Mach2 always knows the true speed of the spindle.

Les


Andy Wander wrote:

I can't speak about the intricacies of the VFD, but PWM is Pulse Width
Modulation, where the ONLY thing that is varied is the width of the "ON"
pulse(not both ON and OFF). This means that the frequency of the pulses
does
NOT change, just the ratio of ON-time to OFF time of a (quasi) square
wave.

If the width of both the ON and the OFF pulse changed(and was identical,
you
would NOT have PWM, you would have FM(frequency modulation) of a square
wave.

Andy Wander
Verrex Corporation




Yahoo! Groups Sponsor


ADVERTISEMENT


Click HereClick Here


<
/S=:HM/A=2019528/rand=293473797>

_____

Yahoo! Groups Links
* To visit your group on the web, go to:

<>

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms of
<> Service.


Les Newell
 

Hi Andy,
If you average a steady state PWM signal (apply a low pass filter) you get a DC voltage. At 0% PWM you get 0V, at 50% PWM you get 1/2 voltage and at 100% PWM you get full voltage and so on.
Now if you slowly change the pulse width your DC voltage will slowly change to follow it.

A VFD changes the pulse width in a sinusoidal pattern and the motor inductance acts as the filter. As long as the PWM frequency is much higher than the sine wave frequency (say 10kHz or highter) all the motor will see is the sine wave. By varying the pattern the VFD can control the sine wave frequency and voltage.

Les


Andy Wander wrote:

Les:
Thanks for the explanation-what I still don't understand about it is how the
"Sine Wave", which is generated by the "filtering" of the motor, will vary
in frequency, if the only thing that is done to it is to change the PWM duty
cycle. This would seem to me to get us to a "Sine wave" which has different
values for it's Positive and Negative half-cycles, but I can't see how the
frequency would change unless the frequency of the PWM changed.
Andy Wander
Verrex Corporation


Art
 

Jeff:

notice that "index pulse" can be checked on the parallel input to
pick up the true speed of a machine. Can the PWM frequency of a VFD
be used for this? If so, can it be scaled in MACH2 to correspnd

No. This can only be gotten for a once per rotation pulse from the spindle
sensor..

Art
www.artofcnc.ca


Ed Gilbert
 

Hi Andy,

Are you actually talking about the signals on the wires to the motor or
about a PWM signal generated by the VFD to indicate the frequency it is
running at?

Mach2 uses the index pulse to determine RPM and is probably based a number
of pulses per interrupt cycle. It may be based on the speeds you define in
the pulley setup of the spindle. You would have to ask ART specifically.



Best,

Ed Gilbert

Gilbert Engineered Systems
632 Warrenton-Embro Road
Macon, NC 27551
252-257-0539

-----Original Message-----
From: Andy Wander [mailto:awander@...]
Sent: Monday, March 01, 2004 12:05 PM
To: 'mach1mach2cnc@...'
Subject: RE: [mach1mach2cnc] Question on index pulse

Of course, VFD means Variable Frequency, so is this actually a PWM signal?
I'm so confused...

Andy Wander
Verrex Corporation

-----Original Message-----
From: washcomp [mailto:jeff@...]
Sent: Monday, March 01, 2004 8:42 AM
To: mach1mach2cnc@...
Subject: [mach1mach2cnc] Question on index pulse

I notice that "index pulse" can be checked on the parallel input to
pick up the true speed of a machine. Can the PWM frequency of a VFD
be used for this? If so, can it be scaled in MACH2 to correspnd to
the speed (I believe speed is a linear function to frequency, but the
numeric value of one will not be the same as the other.

Jeff





Yahoo! Groups Sponsor


ADVERTISEMENT


Click HereClick Here


<
eb
/S=:HM/A=2019528/rand=446470174>

_____

Yahoo! Groups Links
* To visit your group on the web, go to:

<>

* To unsubscribe from this group, send an email to:
mach1mach2cnc-unsubscribe@...
<mailto:mach1mach2cnc-unsubscribe@...?subject=Unsubscribe>

* Your use of Yahoo! Groups is subject to the Yahoo! Terms of
<> Service.







Yahoo! Groups Links






-------------------------------------
This message has been scanned for viruses and
dangerous content by NCOL.NET, and is believed to be clean.